Topic: lithium and agm batteries: a warning !
Posted By: Pzucchel
Subject: lithium and agm batteries: a warning !
Date Posted: 04 July 2025 at 10:11
|
as many of us , I have service lithium batteries and lead agm batteries for the engine starter and generator.
everything worked fine for three years , up to this morning ...when I try to start the engine and the battery wasn't providing enough current to the starter motor. after few minutes of generator , the engine started and I will replace the battery ASAP...
...but I kept thinking about why it happened, and I think I have an explanation.
yesterday it was very hot and I ran the aircon from batteries. I stopped the aircon around 40% about, but it went down overnight to 12% (usually , I never go below 30%).
in my system , the lithium battery is charged by the same chargers (the masscombi and the solar panels) charging the agm, and I never thought what this means: they are subject to the same voltages, therefore they are in parallel!
let's forget for a second about the charger , because that's not what was happening last night.
I checked all the relevant voltages of the discharge cycles and we have three configurations.
lfp soc > 15% (temp. dependent). the service battery has a voltage higher than a fully charged agm battery, so it will trickle charge the agm batteries all the time. the agm batteries therefore never "float", and this reduces the lifetime. I somehow knew it ...but accepted it. this is the normal situation...
SOC around 15%: the voltage of the lfp start going below the fully charged AGM battery , and the agm battery starts charging the lfp battery .. that's 10x bigger , so it's voltage starts dropping and you have an equilibrium for a while...but the agm starts emptying fast ...
SOC below 15%: the lfp voltage drops faster than the almost linear Agm voltage drop , but essentially the AGM battery empties into the Lfp battery than has a larger capacity. now the engine may not start anymore !!!
conclusion: I never explored this regime , but it's clearly not good. the agm battery can be fully discharged by the service battery when the SOC goes below 15%, and that's not what you want.
solution: I will install either a battery charger (like the mastervolt mac plus 12/12-50) or a converter (like the mastervolt magic 12/12-20) to charge the agm batteries...I prefer mastervolt because all components (batteries , mppt, inverter) are mastervolt and I have a czone monitor .
in both devices , I can implement floating for the agm batteries , improving their lifetime and avoiding them to be discharged into the Lfp service battery.
lesson learnt , I hope...
addendum: studying the masscombi 12/2200-100 manual I discovered that there is a secondary 5A charging port...but in my opinion the boat schematics says it's not used , and the battery is attached directly to the main 12V main bus . Am I right or wrong ?
------------- Hanse588#55
|
Replies:
Posted By: Ian Coverdale
Date Posted: 04 July 2025 at 11:43
|
Very interesting.
Paralleling battery chemistries always seemed like a very bad idea to me but there people our there evangelical about paralleling Pb batteries with LiFePO4 to mitigate for BMS going into shutdown when real answer is to have a BMS/monitoring system that alerts user to a potential shutdown condition (as now required by ABYC .. if you like in North America) before the shutdown occurs.
Wonder how your Pb/LiFePO4 batteries parallel. Is that through a battery combiner or a function within your charger? Some (most) auto-voltage sensing battery combiners need upgrading to LiFePO4 compatible models otherwise engine/service parallel at too low a voltage.
Sounds like DC-DC converter to charge Pb from LiFePO4 is the answer.
------------- Ian & Andrea SV Gabrielle (H445) Liveaboards - currently Montenegro. www.facebook.com/sailinggabrielle
|
Posted By: marsella
Date Posted: 04 July 2025 at 11:44
|
I like DCDC chargers. Apparently I see that they take care of my thruster batteries very well. I was also thinking to add one for the engine battery, but where would it go because there is an alternator already which if upgraded does 3 stage charging with Li profile, there is a battery combiner and solar, shore power chargers, which also setup for Li.
|
Posted By: Pzucchel
Date Posted: 04 July 2025 at 13:22
|
I am also very happy of the 12v/24v converters for the thrusters. I was indeed thinking to install the same converter for the engine starter battery but I need to study carefully the schematics. as I mentioned there is also a secondary charger on the inverter that hanse decided not to use:why? Then , isolating the battery with a dc/dc converter would it mean that the alternator stops charging the starter battery directly at high current ? in that case , is 5A trickle charge enough ?
------------- Hanse588#55
|
Posted By: Arcadia
Date Posted: 04 July 2025 at 14:35
Piero, it seems that the engine and service batteries on Andrew are wired together and not via a voltage triggered battery combiner as is on the factory Hanse set up. Also, the alternator is wired directly to the engine battery while the service bank would get charged via the combiner. This set up caused problems for me. I moved the alternator directly to the service bank and modified the combiner so it would trigger with any charge voltage instead of the thresholds that didn’t work. So I’m not sure how your engine and service are combined but they should be separated when not being actively charged. A dc to dc between the service and engine bank is best. But be sure to move the alternator charge cable directly to the service bank along with the other charge sources. The 5 amp from the Mastervolt would be OK but would only charge with shore power or generator, and not the alternator.
------------- Leon / ARCADIA 2018 Hanse 588 Sag Harbor, NY
|
Posted By: marsella
Date Posted: 04 July 2025 at 14:49
|
So just to understand, alternator, solar, and all other charging sources go to the service bank from where 3 DCDC charges go to engine, stern and bow batteries. No battery combiner needed in this case?
|
Posted By: Arcadia
Date Posted: 04 July 2025 at 14:50
Also, be aware that even though the starter battery will deliver many hundreds of amps during starting, the energy consumed is only about 1 amp hour so any size charger will do the job quickly. The bigger issue is that the Volvo D3 on our boats is computer controlled which consumes power as does the blower fan. So a charge current of 25 amps to the engine bank would be sufficient.
------------- Leon / ARCADIA 2018 Hanse 588 Sag Harbor, NY
|
Posted By: Arcadia
Date Posted: 04 July 2025 at 14:54
Yes Marsella. That would work and eliminate the combiner. But as I mentioned, it’s important that the alternator charge cable be moved to the services bank. Otherwise the service bank would not get charged with the engine running.
------------- Leon / ARCADIA 2018 Hanse 588 Sag Harbor, NY
|
Posted By: Arcadia
Date Posted: 04 July 2025 at 14:58
Also, for anyone going in this direction, moving the blower supply voltage to the service bank will greatly reduce the running current supplied by the engine battery (about 20 amps). And because the service bank has the high current alternator connected, the extra load would be minimal there.
------------- Leon / ARCADIA 2018 Hanse 588 Sag Harbor, NY
|
Posted By: Arcadia
Date Posted: 04 July 2025 at 15:01
All this being said, there are many ways to configure the charge sources and the various battery banks and how they interact. No one method is correct, but the important thing is that it works well and addresses the specific needs and concerns of the owner.
------------- Leon / ARCADIA 2018 Hanse 588 Sag Harbor, NY
|
Posted By: marsella
Date Posted: 04 July 2025 at 15:02
|
This looks like a right setup ( the one with 3 DCDCs and all charges to service), one only has to worry about shutting off the alternator if service Li bank gets overcharged and BMS wants to turn off all charging sources, I think smart alternators are capable doing it.
|
Posted By: Arcadia
Date Posted: 04 July 2025 at 15:31
I don’t think there is any real danger with that issue. A multi battery lithium bank will gradually decrease current to zero with each battery shutting off at slightly different times. Any alternator would be able to deal with this. It’s an abrupt disconnect of current that will cause the kind of spike that could damage diodes. Also keep in mind that even with the lithiums at zero charge current, you will still likely have house and navigation loads providing a certain load current as well as the dc to dc chargers.
------------- Leon / ARCADIA 2018 Hanse 588 Sag Harbor, NY
|
Posted By: 32mike
Date Posted: 04 July 2025 at 16:29
|
I have been studying this for a future upgrade to lithium. Here’s what I’m seeing from my research:
I have a generator, so these are in consideration of that. Without one, you may go in another direction.
Option 1 (easiest and cheaper of the two) Alternator from engine is connected to AGM start battery. DC to DC charger (30-50 amp limited) is connected to house bank. Original battery combiner is removed. In this setup, the DC to DC limits the house bank from over drawing the alternator and thus keeps it from overheating. The DC to DC also only operates when the engine is running so that the house bank can’t drain it down to zero. The alternator is protected from a BMS shutdown by virtue of also being connected to the AGM start battery which dampens the shock. The drawback is that my 125 amp alternator is not being used to its full capability in charging the house bank while running. My generator capability backs that up when needed. Also, this eliminates the charging of the AGM start battery on shore or generator power because the DC to DC is one way to the house bank. This limitation can be overcome with a small battery charger which is wired to the shore/generator only output from the inverter/charger. Alternately, you could just wire one solar panel to the start battery only to keep it topped off. I have been told that using the small trickle charger output of the inverter/charger would not be advisable in this setup because when the DC to DC is running, there is a circular current path with that trickle charger - still a little fuzzy on that. This trickle charger is fine to use with the standard all AGM setup but is unnecessary because of the battery combiner which does the trick.
Option 2. (More complicated and more expensive but probably the best setup) Remove the battery combiner. Upgrade to a bigger alternator or keep the same one and install an alternator regulator like a Wakespeed, Sterling or the new Arco Zeus (this one is designed to be used with the bigger alternator for faster charging at idle engine speeds). In this installation, the alternator charges the house bank and the alternator is kept from overheating by the regulator and you can use the full capability of the alternator for charging the bigger house bank directly. A DC to DC is then used to charge the AGM start battery. The alternator is protected from a BMS shutdown by the BMS itself which shuts off the alternator. All the batteries get charged anytime with either shore, gen or engine running.
I don’t run AC’s off of the batteries, so that’s not a problem for me. My bow thruster AGM is charged from a small DC to DC off of the house bank which would just stay that way. From what I have learned, the biggest problem with just keeping the battery combiner and not using a DC to DC between the alternator and lithium bank is that the large lithium house bank can easily overwhelm the alternator because of its very high charge capability. In essence, it can take everything the alternator can give which will cause an over temp and destroy the alternator.
Disclaimer: I am not a marine electrician or even an expert, only an internet researcher (yikes!)
------------- Mike S/V Dulces Sueños 458 #087 Tampa, FL
|
Posted By: 32mike
Date Posted: 04 July 2025 at 16:46
|
Pierro, Take a look at the MasterVolt ChargeMate. If you have this installed instead of the battery combiner, it will prevent the house bank from draining the AGM start battery. The drawback is that you won’t have charging of the AGM start battery unless the engine is running. You could solve that by installing a small battery charger which runs off of the short/gen only output of your inverter charger.
------------- Mike S/V Dulces Sueños 458 #087 Tampa, FL
|
Posted By: marsella
Date Posted: 04 July 2025 at 17:24
|
Mike - option 2 we are talking about. BTW our Valeo 125A alternator can be upgraded with Balmar regulator kit, 1h work to install and there is youtube video showing the steps
|
Posted By: Arcadia
Date Posted: 04 July 2025 at 18:03
Some alternators can deliver more current than they are capable of dissipating. This gives a high output number on paper but not in practice. Balmar is in this category as evidenced by the unusually small cases vs claimed output level. This why they recommend dialing down the charge level with their regulator. I’ve burned up a few in the past with previous boats. I’ve upgraded the Volvo D3 140 amp on mu 588 to a drop in 180 amp unit which can happily deliver full output without overheating. It’s all a matter of how the windings are done internally as well as designing the field current so as not to exceed the heat dissipation capacity. With this set up, I can charge directly to my lithium bank with full output.
------------- Leon / ARCADIA 2018 Hanse 588 Sag Harbor, NY
|
Posted By: 32mike
Date Posted: 04 July 2025 at 18:47
|
Marcella, “ This looks like a right setup ( the one with 3 DCDCs and all charges to service), one only has to worry about shutting off the alternator if service Li bank gets overcharged and BMS wants to turn off all charging sources, I think smart alternators are capable doing it.”
This is what I understand is the weak spot in this setup. From what I’ve read, if the BMS shuts off charging while the alternator is charging, it could disable the alternator. By connecting the alternator to the AGM and then to the house bank through a DC to DC, the AGM absorbs the shock(?) of the lithiums shutting off the in-current.
Questions for you - how is your alternator hooked up now? Have you added the Balmar alternator regulator or just thinking about adding it? Do you still have the combiner?
------------- Mike S/V Dulces Sueños 458 #087 Tampa, FL
|
Posted By: marsella
Date Posted: 04 July 2025 at 19:31
|
My current setup is our original alternator but with a replaced regulator from Balmar that is programmed for Li profile. I also have a Victron battery combiner, which replaces the original combiner from Hanse. The only difference is that the victron conbiner can disconnect if BMS tells it to do so. The downside I see that engine battery is charged by Li profile but I think is not a big deal since AGMs can be abused.
In the setup which we talk here the alternator and all other charging sources are directly connected to service bank.For alternator one can lower the voltage of the combiner as Arcadia said (not sure if I can reprogram the victron combiner for this) or just remove the combiner. At the same time DCDC charger is inserted to charge engine battery same as DCDC chargers do for thrusters. I think its a nicer setup which alllows proper charging profiles for all components. I have to think more if there is any downside going that way but its easy to hook everything this way, just need to buy another DCDC from Victron.
|
Posted By: Pzucchel
Date Posted: 06 July 2025 at 09:09
|
as usual , Leon is right. I think there is a battery combiner, called in the schematics batterie combiner 8K1, that should disconnect the engine battery from the service bus in certain conditions first trivial question: where is it ? second trivial question: what model is it and how it works? what's the impact of replacing lead batteries with lithium: will it still work?
this could change my analysis. let's assume it works correctly: the lithium bank went down in voltage , the starter battery was disconnected from the bus...and my battery is "tired", e.g. subject to sulfation because I don't float it (my settings are for lithium). then it didn't have the crank capacity that it has when the two buses are connected...thanks to the lithium!
now I also understand why Leon insists on moving the alternator to the service battery. the battery combiner may separate the alternator from the service battery, making recharging the service battery when the service battery goes down impossible with the engine. still , in my boat solar panels and generator will charge it.
in practice, what does it mean to move the alternator onto the service battery: deploy 200A cables from the engine room to the service battery?
------------- Hanse588#55
|
Posted By: marsella
Date Posted: 06 July 2025 at 10:01
|
The combiner is very close to positive busbar of the service bank on 458 so I think its similar on all boats. And you dont need to add any cables, the cables from the alternator to the service bank are there already. You either remove the combiner or lower its voltage which Im actually not sure is possible but Leon said so. Would love to hear how exactly it can be modified.
|
Posted By: 32mike
Date Posted: 06 July 2025 at 13:38
Pzucchel wrote:
as usual , Leon is right. I think there is a battery combiner, called in the schematics batterie combiner 8K1, that should disconnect the engine battery from the service bus in certain conditions first trivial question: where is it ? second trivial question: what model is it and how it works? what's the impact of replacing lead batteries with lithium: will it still work?
Yes, there is a battery combiner - here is the one I have. Like Marsella said, it is installed in the battery compartment, right between the service batteries and the positive bus bar.
now I also understand why Leon insists on moving the alternator to the service battery. the battery combiner may separate the alternator from the service battery, making recharging the service battery when the service battery goes down impossible with the engine. still , in my boat solar panels and generator will charge it.
The battery combiner will still work as advertised whether the alternator is connected to the start battery or the service bank even with lithium service batteries. There are four potential problems though that arise with lithiums installed. First, the lithiums can charge at a much higher rate than AGM’s and they can overload and overheat the alternator. Second, the lithiums charge profile for lithiums is different than AGM’s. Third, if, you remove the combiner and separate the two banks, you need to manage the charging in a different way than the simple combiner. This is usually accomplished with some version of a Dc-Dc charger between the banks - it is a one way switch and can be set for the correct charge profile. Fourth, the lithiums have a BMS, either internal or external which controls things like charging and if the BMS decides to cut off charging while the alternator is producing a significant amp load, you can get a “load dump” which can ruin the alternator. So, you can leave the alternator on the start battery and charge the lithium bank with a Dc-Dc - this protects the alternator but limits your service bank charging to 30-50 amps and it also limits charging of the start battery to only when the engine is running. Or you can move the alternator to the service bank and charge the start battery with a Dc-Dc from the service bank. In this setup you will now have start battery charging anytime the service bank is being charged. The big drawbacks are that the alternator is now not being protected from overdrawing overheating from the lithium bank and if the BMS decides to shut off charging, the alternator and DC load bus is not protected from a “load dump” which can damage the alternator and other electronic devices. The most common way of solving this is through an external alternator regulator controlled by the BMS. The regulator keeps it from overheating and the BMS will shut down the alternator properly through the regulator without getting a “load dump.”
in practice, what does it mean to move the alternator onto the service battery: deploy 200A cables from the engine room to the service battery?
As Marsella said, this cable is already in place if you elect to modify. A cable runs from the alternator already to the combiner right next to the battery. It could then be connected either to a Dc-Dc charger to the service positive bus bar or directly to the service bus bar depending on how you wish to construct your system.
|
------------- Mike S/V Dulces Sueños 458 #087 Tampa, FL
|
Posted By: marsella
Date Posted: 06 July 2025 at 14:12
|
My understanding is that DCDC should go into engine room or close, where another end of the alternator cables are now connected to the engine bat. Thats where DCDC should be inserted. I think engine room is not a good location becaue it gets hot and DCDC gets hot, but somewhere around it.
|
Posted By: 32mike
Date Posted: 06 July 2025 at 15:13
marsella wrote:
My understanding is that DCDC should go into engine room or close, where another end of the alternator cables are now connected to the engine bat. Thats where DCDC should be inserted. I think engine room is not a good location becaue it gets hot and DCDC gets hot, but somewhere around it.
|
For the Victron Dc-Dc, the manuals say to mount close to but not above the battery (which is a lead acid thing with potential off-gassing). Heat is an issue. The smaller 30 amp units apparently get very hot and many people in vans and boats installed ventilation fans. The newer 50 amp units don’t get as hot but the manual says it can get up to 90C and to mount on a surface that can withstand that temperature.
------------- Mike S/V Dulces Sueños 458 #087 Tampa, FL
|
Posted By: Arcadia
Date Posted: 06 July 2025 at 15:38
Piero, the combiner activates based on a threshold voltage of about 13.2 v. So the service bank will not engage until the engine battery reaches 13.2. So often when the much larger service bank engages, the voltage can then drop back below threshold and will open the combiner. This cycle can repeat over and over if the service bank is heavily discharged. Bad design !!
------------- Leon / ARCADIA 2018 Hanse 588 Sag Harbor, NY
|
Posted By: Arcadia
Date Posted: 06 July 2025 at 15:48
There is heavy cable that brings the charge current from the alternator to the combiner near the positive bus bar. You can repurpose that cable as a direct connection. I then moved my combiner to a location near the engine battery to control its charge. No more cycling. The combiner won’t engage until the service bank reaches a good charge level.
------------- Leon / ARCADIA 2018 Hanse 588 Sag Harbor, NY
|
Posted By: Arcadia
Date Posted: 06 July 2025 at 15:57
Also forgot to mention. My combiner no longer uses threshold voltage. There is a separate trigger input that will activate the combiner. I ran a trigger voltage from the engine blower and also from my battery charger so that the combiner will engage whenever charging takes place.
------------- Leon / ARCADIA 2018 Hanse 588 Sag Harbor, NY
|
Posted By: 32mike
Date Posted: 06 July 2025 at 16:30
Arcadia wrote:
Piero, the combiner activates based on a threshold voltage of about 13.2 v. So the service bank will not engage until the engine battery reaches 13.2. So often when the much larger service bank engages, the voltage can then drop back below threshold and will open the combiner. This cycle can repeat over and over if the service bank is heavily discharged. Bad design !! |
I think it works fine with AGM’s on both sides of it. There is built in delays for connect and disconnect. It engages at 13.2v and disconnects at either 12.8 after 60 seconds or 11.8 after 4 seconds. I would also think, that with the alternator running and putting out good amperage, even the discharged lithium bank wouldn’t pull the voltage down below 12.8 for a solid minute, but I could be mistaken on that. In any case, this is really an AGM device. Most lithium designs these days don’t incorporate a battery combiner at all. I’ve even seen setups where people completely separate their AGM start battery from their lithium service bank just to simplify things.
I think the big stumbling blocks with adding lithium to our previous all-AGM boats is the different chemistries/ charge profiles and the fact that the alternators were designed for lead/acid batteries - they don’t have lithium charge profiles built in and they don’t have an installed shutoff that the new lithium BMS can activate when needed to safely cut off the charge under any circumstances. So, we need to start jury-rigging things by adding or subtracting devices to overcome the stumbling blocks. I’m still struggling with the possibilities with an eye for keeping it as simple as possible while still covering all bases with the minimum of modifications and money spent. It’s a challenge!
------------- Mike S/V Dulces Sueños 458 #087 Tampa, FL
|
Posted By: marsella
Date Posted: 06 July 2025 at 18:45
Arcadia wrote:
Also forgot to mention. My combiner no longer uses threshold voltage. There is a separate trigger input that will activate the combiner. I ran a trigger voltage from the engine blower and also from my battery charger so that the combiner will engage whenever charging takes place. |
I think one can just replace the combiner with a solenoid, something like Lewmar el.winch contactor would have a right amperage for this. In this case as long as BMS allows charging sources, the contactor is closed, and the alternator charges the service bank. When BMS signals to stop charging, the contactor will just open.
|
Posted By: Pzucchel
Date Posted: 07 July 2025 at 09:53
|
update: I confirm I do have a battery splitter. it's a different model from the ones described here , it's the mastervolt chargemate 2502 and it does sit nearby the service battery compartment bus.
you can see the manual here : it's configured in automatic mode.
https://images.mastervolt.nl/files/ManualChargeMate2502_090205.pdf" rel="nofollow - https://images.mastervolt.nl/files/ManualChargeMate2502_090205.pdf
It seems it has histeresis and delay features preventing flipping on and off, and very interestingly one could both wire a manual switch , overriding the off position allowing to start on the service battery , and even an indicator /czone information to know what's happening without taking the sofaaway ...
I checked all the cables , and I confirm whatever had been said above by 32mike, Marsella and Arcadia.
in my system I have two additions: 2x mppt, on the service bus , charging the service battery, and another battery that's used to start the generator.
in particular , the agm generator service battery is completely in parallel of the engine battery. there is no battery splitter. I was puzzled by this : when I had the problem I couldn't start the engine , but I could start the generator. this is probably simply because the crank requirements are lighter. then , I realise I have an old agm battery in parallel to a new one : I'm sure it's a bad idea , the new battery may be continuously discharging into the old one ...
going back to my original problem , I start suspecting that the sequence of events was: the service battery went below 13v, it disconnected from the engine battery and the generator battery. then the engine battery discharged partially even if fed by the generator battery (higher internal resistance because of lower CCA) ...and both couldn't provide the cranking current. when I started the generator , the splitter went on and the 10kWh lithium batteries covered the engine battery problem...
now I need surely to replace the engine battery , it shows some sulfation signs on the contacts .
..and now I know that I can overwrite the battery splitter and use the service batteries to start the engine!
as a last piece of information , I even have 2x masterbus controlled isolators (ml-rbs from ocean systems) on the lithium batteries: they are programmable with masteradjust, and I currently use it for last resort discharge below 10% and thermal limit. it rarely happens , and I think this is what is described here as a abyc requirement.
ultimately , I could redesign the system ...but admittedly it worked flawlessly for 4 years , up to the moment the engine battery got old (the battery was used for 5 years ) so you could understand my hesitation: don't break what works !
I know the current limitations now:
1) agm batteries , generator and engine , aren't optimally using ideal bulk/abs/float timings and voltages...but this deserves another thread, because the differences been lfp and agm settings are not very big.
2) the two agm batteries are in parallel without a split. is this what I want/like ? the two batteries aren't identical in capacity...
3) potentially and theoretically, the lithium batteries could disconnect from the alternator when the engine is running creating load jumps that may affect the alternator. admittedly , this should happen only on very rare situations, and the BMS should anyway have priority because of safety
------------- Hanse588#55
|
|